1.it is used to delay the appliance on timing.it is basically used to avoid spike startup of appliances when the power is restored.

  1. 1000 is the count for 1 second so for 500 it will be half second delay and for 3000 it will be 3 second delay.

3.it will work with physical as well as from the app.

  1. 16Amp is used for heavy appliances hence delay is not required.
2 Likes

As shared screenshot, not showing complete message.

You given prompt reply.

Thanks @Sanket

The Switch Delay is basically a delay added to the manual switches . This delay is required so that whenever the power goes and comes back within milliseconds , the device should not turn on the load. To prevent this, a delay check if the manual switch is ON for the specified delay before turning ON/ OFF the load

16A also has a manual switch , so switch delay is required. with v7.0 firmware you can change switch delay

1 Like

In my 6 channel relay it is showing in percentages although at the bottom it says 2000 units recommended and all that…what percentage should I keep?

We have changed from units to Percentage. If your nodes doesn’t automatically turn ON/ OFF whenever there is power fluctuations. You can lower the delay . If it happens then keep on increasing the delay.